IEC 60502-2/2005
10.2 Requirements
The dimensional, physical and electrical requirements of the metallic screen shall be
determined by national regulations and/or standards.
Usually the IEC Standard cable manufacturers present the screen area and the screen short-circuit withstand current in their catalogue.
If you intend to follow IEC 60287 calculation way you need Rs indeed. No IEC Standard indicates how to calculate.
In my calculation I used the ICEA P-45-482 as presented by cuky2000 calculating the tape width from the formula:
For Helically applied flat tape ,overlapped.[new cable, good contact ]
usually the tape winding angle is between 60 to 70 degrees.
W = 100 / (100 - OVL) .π . dm . Cos(70 / 180 * π)
A = 4 * THK * dm * Sqr(100 / 2 / (100 - OVL))[mm^2]
OVERLAP [%]=; OVL
SHIELD DIA[MM]="; dm
SHIELD THICKNESS[MM]="; THK
The French Standard HN-33-S-52-for instance- presents a formula for screen resistivity :
ρ1=R1.π.(d-T1).T1/2L
and from here:
R1=2.ρ1.L/[π.(d-T1).T1] where:
R1=measured resistance
L=the distance between the measured points[the length in m]
d=insulated core diameter[m]
T1=screen average thickness [m]