Hi, all
Are there any NFPA terms stipulating the conditions of using either natural or mechanical Smoke extraction system? For example,as per my local fire standard, a mechanical smoke extraction system shall be used if the floor area exceed 50sq meter if without windows, so I wonder are there similar codes in NFPA?
Thanks a lot!
 
NFPA 1:11.8 outlines the installatioan an care of these systems, "where installed".

Individual occupancies may speak to requirements for "smoke control" systems. Here are a couple:
Mercantile Occupancies, NFPA 101:36.4.4.12, required in mall concourse with floor openings connecting more than 2 stories.
Smoke protected assembly seating requires a smoke control, NFPA 101:13.4.7.5.1.
New healthcare occupancies speak to the requirement for an engineered smoke control system, NFPA 101:18.7.7
There are multiple other chapters and occupancies that speak to this in the same way.
 
Thanks a lot for you kind help!
 