Arch-pipe as Pond Outlet?

Status
Not open for further replies.

Granny36

Civil/Environmental
Jun 29, 2004
10
Has anybody tried to model an arch pipe or anything other than the standard circular or rectagular as a culvert outlet? If so, I'd sure like to find out how you did it.

Thanks
 
Replies continue below

Recommended for you

If you open the culvert screen in HydroCAD and click the Help button you'll get some suggestions for modeling an arch pipe.
 
Granny:

As psmart points out, the help system suggests using the overall pipe dimensions with a 0.9 multiplier for arch pipe or 0.8 for eliptical pipe.

However, when I am dealing with finicky regulators, I use a "Special User Defined" outlet and supply data from HY-8.
 
A custom device will work fine - as long as you're not dealing with variable tailwater. But if the flow is tailwater-dependent, then you'll need to use one of the standard outlet devices, whose equations can handle the extra variable.
 