tctctraining
Electrical
- Nov 17, 2008
- 118
I ran a study using SKM software,results show Cat2 for data given at 80% of the maximum fault level as a worst case senario.( Incident energy was calculated 6.2 cal/cm2)
The tcc curve of the fuse does not clear the cat#2 PPE curve after 1 second,however the same fuse clears cat#3 curve for 2 second escape time, so the adequate PPE will be cat#3 if the 2 second escape time is considered.
if a different approach without considering the 2 second escape time is taken then at 80% of the fault level cat#2 is adequate.
Does anyone considers the 2 second escape time when assignining the PPE clothing and arc flash study?
Is there any refernce in IEEE or anywhere else to this matter?
Thank you
The tcc curve of the fuse does not clear the cat#2 PPE curve after 1 second,however the same fuse clears cat#3 curve for 2 second escape time, so the adequate PPE will be cat#3 if the 2 second escape time is considered.
if a different approach without considering the 2 second escape time is taken then at 80% of the fault level cat#2 is adequate.
Does anyone considers the 2 second escape time when assignining the PPE clothing and arc flash study?
Is there any refernce in IEEE or anywhere else to this matter?
Thank you