HokieStructural
Structural
- Apr 24, 2007
- 5
The commentary for Section D.6.2.1 states that shear breakout will not control for anchors that are "far from the edge." I'm looking for guidance on how far an anchor should be from the edge in order to neglect shear breakout. For example, I'm calculating a shear breakout capacity of only 50 kips for an anchor in the middle of an 8'x8'x2'-thick footing. Judgement tells me this is rediculously conservative, but the numbers say otherwise. Has anyone else dealt with this?