API RP 505 , ACH for Hazardous Areas 1

Status
Not open for further replies.

yartes

Mechanical
Joined
Apr 2, 2004
Messages
5
Location
CA
Based on API RP 505, the recommended ventilation for hazardous and non-hazardous areas is 12 and 6 ach respectively. From a Fugitive Emissions study I came up with only 2ach required for adequate ventilation. What flow rate I should apply? The recommended or the calculated?

Is that recommended ACH for the "whole room" or just the zone 1 area limited by the extensions suggested by API RP 505?

Please help... :-/
 
Did you actually read API RP 505? Especially sections 6.6 and Appendix B give quite clear guidelines on how to determine whether an enclosed area is adequately ventilated.

As per section 6.6.2.4.8, an enclosed location is adequately ventilated if a detailed calculation as per Appendix B shows that fugutive emissions concentrations remain below 25% of LFL. If calculated number of Air Changes per Hour is less than 3 it is recommended to provide continuous monitoring with fixed gas detectors.

I would say the whole room has to be adequately ventilated, since if this was not the case, the whole room would become zone 1...
 
Thanks Guidoo for your answer!

I have one simple question: If an enclosed-space is classified as Class 1, Zone 1, but the electrical equipment within this area is designed for Zone 1, Do I still need to ventilate at all??? ...or regardless of this I need to ventilate with the calculated flow from the fugitive emmissions study?

Thanks for your invaluable answer!


 
Yartes,

It is difficult to understand your question, but it seems like you mean this:

"If the enclosed area is classified as zone 1 based on the assumption that there is no adequate ventilation, do I still need to ventilate the enclosed area?"

The answer is no. You either have adequate ventilation or non-adequate ventilation. If you have non-adequate ventilation you can also have no ventilation at all (for area classification reasons). Note that there will normally always be some form of natural ventilation...
 