Lets consider an API650 tank 83 m diam x 20 m ht
New API 6550 11th § 7.3.6.6 provides with allowable settlement criteria at hydrotest for new tanks :
- Differential settlement <= 13 mm per 10 m of circumference,
- Uniform settlement <= 50 mm
These criteria seem to be very stringent compared to the ones applied in the past as :
- Differential settlement : Pr De Beer criteria (1969)
?si/L ? 1/450 ; With ?si : Relative deflection between 2 points distant from L ; so :
For L = ? D / 28 = 9,313 m, ?si = 9.313 / 450 = 20 mm,
For L = 10 m , about 22 mm (instead of 13 with API 650 11th)
- Uniform settlement : to avoid piping connection deformations : 300 mm (no standard)
Does somebody have any feed back about API650-11th settlement criteria applicability on recently built tanks, particularly the differential settlement?