Mike20

Mechanical
Dec 10, 2012
2
My project has specified several 5 - 8 MW, 2-pole (3564 rpm) induction motors. The lateral analyses on these motors predict coupling-end vibration at the following:
- 4113 rpm, 3rd mode shape(exceeds run speed by 15.4%) - Motor A
- 7186 rpm, 4th mode (within 1% of 2X run speed and 2xLF) - Motor B
- 1843 rpm, 3rd mode shape (within 5% of 1/2 X run speed and 1/2 X LF) - Motor C

I plan to request an Unbalance Response Test (with weights placed at the coupling per API 541 4th Ed., Section 4.3.5.3) for Motor A. The test would be run to 120% of rated speed. In doing so, we would confirm the 15.4% separation margin.

Question - Would the Unbalance Response Test be worthwhile for Motors B and C if I'm concerned about 1/2X and 2X run speed and line frequency? Would the unbalance (1X) excite the 3rd and 4th modes (1/2X and 2X) of these motors and provide any meaningful information?
 
Replies continue below

Recommended for you

No. Unless you have really horrible mechanical problems adding unbalance can only excite at the run speed.

Cheers

Greg Locock