ChemEngSquirrel

Chemical
Jun 10, 2010
72
What discharge coefficients are recommended for low pressure tank PSVs when designed to API 2000?

This is for preliminary sizing. Service is gas. For API 520 I'd use 0.975 but not sure this applies to an API 2000 psv.

Thanks.
 
Replies continue below

Recommended for you

I usually just use the capacity charts from Enardo or Varec or others. I might curve fit them to automate the calculation process. Then the discharge coefficients are unimportant to me.
 
In the old days, we used an orifice discharge coefficient of 0.5 for preliminary sizing. We also used a "rule of thumb" that the sizing pressure had to be 2X the set pressure to guarantee the pallet was wide open.

Nowadays, in the 6th Ed. (Nov. 2009) of API 2000 I glanced at, they show a graph of discharge coefficient (Y) versus absolute pressure ratio (X) of inlet P / outlet P. For X from 0.5 to 1.0, Y ranges from 0.825 to 0.65, respectively. This is from the curved labeled valve discharge coefficient for published capacity.


Good luck,
Latexman

To a ChE, the glass is always full - 1/2 air and 1/2 water.
 