Any risk of Flash corrosion in my Cooling Tower? 1

Status
Not open for further replies.

Karbone

Chemical
Joined
May 10, 2007
Messages
5
Location
BG
I have a chemical softening/clarifier pre-treatment design for my Cooling Tower that produces corrosive water. After reaching steady state, the CT water quality calculation shows a scaling LSI.

Should I be dosing corrosion inhibitor during start up to avoid flash corrosion?

Any tips would be highly appreciated.

Karbone
 
You really should look into obtaining the services of a competent water treatment chemical provider. Someone from a Betz, Chemtreat, etc. will be able to initiate a proper chemical treatment program for the cooling tower. A corrosion inhibiter, a biocide, maybe an acid feed system to control alkalinity, etc, will be part of that program.

Here is a reference on cooling tower startup:

"Proper startup of cooling tower systems prevent initial corrosion and fouling"

THe cooling tower manufacturer should also provide some assistance. Here is a link that provides typical startup instructions:
 
Thank you so much Bimr for your valuable tips. We are still in the construction phase but I want to be better prepared come commissioning.

Best regards,

Karbone
 