Any advantage using Cable Limiter on SST for HV Substation

Status
Not open for further replies.

cuky2000

Electrical
Joined
Aug 18, 2001
Messages
2,135
Location
DO
Does anyone see any benefit of using a cable limiter on the secondary side of the station service transformer in a HV substation application?

Notice that there is a primary fused disconnect switch with 350A CL fuses. This is an interim installation with removal schedule in the ultimate design schedule in a couple of years later.

Cable_Limiter_zjxsvg.jpg
 
The only benefit I see would be to reduce the incident energy at the Safety Switch if that is to be used to verify de-energized on the secondary side for LOTO. Otherwise the only protection from an arc flash or other short circuit is the primary side protection which would be slower.
 