Ron74 said:
Any advantage to higher voltage motors?
The rule of thumb is when the motor Horse Power is higher than the voltage it is time to run the numbers on a higher voltage motor.
If your motors are less than about 500 HP each, don't worry about high voltage.
Also, in this instance when we talk about higher voltages we are talking about moving up from 480/600 Volts to 4160 Volts or more.
If you are comparing motors in the lab, you can quantify the slight possible difference between a 460 Volt motor and a 575 Volt motor but you are not doing a laboratory analysis. You, as I understand it, are selecting a motor to purchase.
MATCH THE MOTOR TO THE AVAILABLE VOLTAGE.
As an example; If you select a 575 Volt motor because of greater efficiency over a 460 Volt motor, you will need a transformer which will erase any savings in initial motor cost and running efficiency many times over.
The perceived advantage of a 600 Volt motor over a 460 Volt motor is a fine point.
The added losses of a transformer to run a 575 Volt motor with a 480 Volt supply is a GROSS point.
You mention a DC power supply and a 150 kW load as well as motors below 10 kW.
You may have unasked and unanswered questions in addition to motor voltage.
What are you designing/building?
Bill
--------------------
"Why not the best?"
Jimmy Carter