I believe that there should be a brief discussion on types vortex breakers here...
What "nabeel3" has pictured in his question is a perfectly acceptable "X type" device for pump protection in the process industry, where pump suction must be taken from a relatively small volume,..... a potable water tank.
The process industry has
NO SPECIFIC DIMENSIONAL GUIDELINE to determine the configuration of a VB, like for example the ASME Dimensional codes for piping flanges. There are only company developed "rules of thumb and recollections of Geezers. Some companies have "pancake" cross, single plate and other configurations
There have been many discussions on this fora on Process System Vortex Breakers
There are also guidelines in the "Hydraulic institute Standards" on Vortex Breaker and Sump Configurations.
Now we come to the NFPA Requirements ..
NFPA 20 and 22 discuss particular types of "donut" or "pancake" VB ......
BUT BOTH STANDARDS ASSUME THAT THE SUMP/TANK IS LARGE, QUIET and a MINIMUM SUBMERGENCE IS MAINTAINED.
Some Alternative design examples are here: .......
Will these work in all circumstances, I do not know....
But I do know that it would probably be wise to distinguish between a "
process system vortex breaker design " and an "
NFPA Vortex breaker design"
Anyone have anything to add here ????
MJCronin
Sr. Process Engineer