jmaddox
Civil/Environmental
- Mar 20, 2013
- 8
So, I am trying to make sure that I have all of my bases covered. I am verifying the anchorage of some elevated mechanical equipment to an interior 6" SOG reinforced with #3 @ 18"oc. I calced the T/C force to be 974# per base plate and the contractor used 4- 1/2" x 6" Redheads and an 8"sq base plate. I checked the bolts for combined shear and tension and get a ratio of 0.57. So the anchors work. My question is: Can the reinforced SOG take the uplift? The area of concrete required to hold down 974# with 0.6DL factored in is about 4'-9". Can I assume that the rebar will engage the reqd concrete? Is there a calculation that that determines the maximum area of SOG that can be engaged?
Thanks in advance for any help.
Thanks in advance for any help.