BSVBD
Structural
- Jul 23, 2015
- 463
There are a variety of anchors for hollow core material applications to CMU, brick, plank and panel.
However, depending on the application:
1. The allowable loads are very low to accomplish the necessary load.
2. The tabulated allowable loads are for anchors installed in hollow core concrete with a minimum compressive strength of 7,000 psi. Spancrete specifies its concrete to be 5,000 psi. Therefore, how can i specify an anchor with such a waiver? Can we interpolate the values? And if so, the result would be that much lower.
3. On-site testing is required to determine the actual performance of the anchor. This does not make it practical to specify an anchor in the office to obtain state approval.
Does anyone have a dependable and satisfactory method or anchor manufacturer to recommend?
Among others that i do not recall at this time, I've specified the following:
- Rawl / Powers / Simpson Drop-ins which actually have a "better" allowable tension, but, the main contractor i have been working with complains that the drop-ins tend to spin within the material. That was years ago and i will need to re-investigate that with more than one site foreman. Has anyone else had this complaint? The allowable tensions for drop-ins are better than most anchors for hollow core, BUT, i've stayed away because of ONE complaint. In general, ONE failure is typically enough! Any comments on this?
- Tapcon / concrete / masonry screws which have a low tensile value for hollow core material.
- Hilti screen-tube sleeve anchors with threaded rod and epoxy. Again, the allowables are low.
I DO understand the proprietary reasoning behind the low values. I'm just researching for a better solution and resource than what i currently have.
Any assistance will be appreciated.
Thank you!
However, depending on the application:
1. The allowable loads are very low to accomplish the necessary load.
2. The tabulated allowable loads are for anchors installed in hollow core concrete with a minimum compressive strength of 7,000 psi. Spancrete specifies its concrete to be 5,000 psi. Therefore, how can i specify an anchor with such a waiver? Can we interpolate the values? And if so, the result would be that much lower.
3. On-site testing is required to determine the actual performance of the anchor. This does not make it practical to specify an anchor in the office to obtain state approval.
Does anyone have a dependable and satisfactory method or anchor manufacturer to recommend?
Among others that i do not recall at this time, I've specified the following:
- Rawl / Powers / Simpson Drop-ins which actually have a "better" allowable tension, but, the main contractor i have been working with complains that the drop-ins tend to spin within the material. That was years ago and i will need to re-investigate that with more than one site foreman. Has anyone else had this complaint? The allowable tensions for drop-ins are better than most anchors for hollow core, BUT, i've stayed away because of ONE complaint. In general, ONE failure is typically enough! Any comments on this?
- Tapcon / concrete / masonry screws which have a low tensile value for hollow core material.
- Hilti screen-tube sleeve anchors with threaded rod and epoxy. Again, the allowables are low.
I DO understand the proprietary reasoning behind the low values. I'm just researching for a better solution and resource than what i currently have.
Any assistance will be appreciated.
Thank you!