Can anyone see any issues with calculating the thread capacity of a anchor bolt nut that is not fully engaged and comparing it to the applied load to determine if it is acceptable?
The anchors are 1" diameter Red Head anchors and are oversized for the loads they will see (approximately a 3:1 ratio of allowable concrete breakout capacity to applied load). The engagement is a little above one half the nut and the thread capacity is higher than the conrete breakout. Installing a coupler is not possible and I doubt that the bolt material is conducive to welding.
The anchors are 1" diameter Red Head anchors and are oversized for the loads they will see (approximately a 3:1 ratio of allowable concrete breakout capacity to applied load). The engagement is a little above one half the nut and the thread capacity is higher than the conrete breakout. Installing a coupler is not possible and I doubt that the bolt material is conducive to welding.