I am looking for your feedback regarding the anchor bolt spacing on residential basement walls (North Carolina). I know that lateral load issue has been discussed but I see no reference to the anchor bolt spacing issue.
The NC Building code (adapted from the IBC) in Section 1610 Soil Lateral Loads states “Basement walls and other walls in which horizontal movement is restricted at the top shall be designed for at-rest pressure” and “Exception Basement walls extending not more than 8 feet below grade and supporting flexible floor systems shall be permitted to be designed for active pressure” The table gives the at-rest values for sandy gravelly soils as 60 psf and clay type soils at 100 psf.
Using the above with a wall 10’ (most of the walls exceed the 8’ number) from ftg. to sole plate with 9’-4” retained soil that gives a load at the top of the wall of app. 812 lbs.
Using the National Design Spec for wood members a ½” bolt and a Southern Pine sole plate of 1-1/2” thick has a value of 410# that would mean that ½” bolts would have to be 6” o/c. The code calls for anchor bolts at 6’ max.
I know that there is also friction resisting value but that is somewhat minimal especially if the floor framing is parallel to the foundation wall.
In our area for years thy never even used anchor bolts and the wall did not collapse.
Please give me your insight.
The NC Building code (adapted from the IBC) in Section 1610 Soil Lateral Loads states “Basement walls and other walls in which horizontal movement is restricted at the top shall be designed for at-rest pressure” and “Exception Basement walls extending not more than 8 feet below grade and supporting flexible floor systems shall be permitted to be designed for active pressure” The table gives the at-rest values for sandy gravelly soils as 60 psf and clay type soils at 100 psf.
Using the above with a wall 10’ (most of the walls exceed the 8’ number) from ftg. to sole plate with 9’-4” retained soil that gives a load at the top of the wall of app. 812 lbs.
Using the National Design Spec for wood members a ½” bolt and a Southern Pine sole plate of 1-1/2” thick has a value of 410# that would mean that ½” bolts would have to be 6” o/c. The code calls for anchor bolts at 6’ max.
I know that there is also friction resisting value but that is somewhat minimal especially if the floor framing is parallel to the foundation wall.
In our area for years thy never even used anchor bolts and the wall did not collapse.
Please give me your insight.