Here are some of my issues with pre engineered buildings:
I agree with you with your comment "However, in every case I've seen, the snow exceeded the code prescribed load". However the "prescribed" load is a minimum. To not include any additional load other than what is exactly on the structure (which appears to be the standard practice) is a bit scary to me. I doubt as a designer you know exactly where a HVAC guy is going to put his duct. To design to the absolute minimum (while within guidelines) assumes that structural construction is perfect, that you know exactly where all loads are, and that the owner will not hang any additional load. I don't agree that you can assume all of those at the same time.
It also appears (IMO) that many of these designs are outsourced to other countries (in most cases India). A few years ago i had a project (i had to design the foundation) where after I sized the foundations i realized that one of my foundations was considerably smaller than i expected for the bay spacing. After several hours of review, the designer had designed the middle column supporting a continuous beam to support 5/8 of the total load(the end beam reaction). After several conversations with the actual designer (who couldn't understand the concept of "trib width") i called the person who signed the drawings and he immediately apologized and thanked me for noticing (the column would have failed under the normal snow load). The designer didn't realize that the 5/8 in the steel manual was the reaction at each beam, not the total reaction at the middle.
I believe that PEB IF designed properly will only meet the absolute minimum. I wonder how many of your clients understand what exactly is meant when you say minimum.