I have this situation:
I have a seametrics ex215b flow meter with a seametrics ft420 totalizer with 4-20ma output.
I have interfaced this with a red lion signal conditioner to change the 4-20ma to 0-20ma.
I then have it wired into a Netbiter EC220 analog input which I set the dip switches for 0-20ma.
Now for the hard part, what vaules do I set for scaling?
where 0.00ma = 0 gallons per minute
and 20.00ma = 1400 gallons per minute
my question is what would my scaling and offset be?
min. flow in this 14" pipe is 134gpm, this is the rate at which the influent water begins to be measured... and the maximum is 1,400 gpm.
but I just cant seem to figure it out...here are some pictures of what I have going on.
I have a seametrics ex215b flow meter with a seametrics ft420 totalizer with 4-20ma output.
I have interfaced this with a red lion signal conditioner to change the 4-20ma to 0-20ma.
I then have it wired into a Netbiter EC220 analog input which I set the dip switches for 0-20ma.
Now for the hard part, what vaules do I set for scaling?
where 0.00ma = 0 gallons per minute
and 20.00ma = 1400 gallons per minute
my question is what would my scaling and offset be?
min. flow in this 14" pipe is 134gpm, this is the rate at which the influent water begins to be measured... and the maximum is 1,400 gpm.
but I just cant seem to figure it out...here are some pictures of what I have going on.