We have a linear pot that precisely measures position. The pot is fed from a precision 10VDC source, and is fed into a ±10V analog input card (14-bit resolution; only 13 bits are utlized since the signal is 0-10V).
My idea is to do away with the 10V source and instead use the pre-existing 24VDC power supply source, running the pot output to a 0-30V analog input card (14-bit). This card has two channels--the second channel, currently unused, would have the 24V line running in to its analog input directly. This way I could take the ratio of the pot output to the 24V signal and remove any fluctuations in line voltage.
This should result in a 60% increase in resolution, plus do away with the 10V power source.
The 10V and 24V supplies both have a 0.5% line regulation, and 0.7% and 0.5% load regulation respectively. Of course the load on the 24V supply will vary much more greatly.
Both cards are differential input, although that shouldn't really matter.
Is this a bad idea? What are some caveats I am not thinking of?
Thanks!
My idea is to do away with the 10V source and instead use the pre-existing 24VDC power supply source, running the pot output to a 0-30V analog input card (14-bit). This card has two channels--the second channel, currently unused, would have the 24V line running in to its analog input directly. This way I could take the ratio of the pot output to the 24V signal and remove any fluctuations in line voltage.
This should result in a 60% increase in resolution, plus do away with the 10V power source.
The 10V and 24V supplies both have a 0.5% line regulation, and 0.7% and 0.5% load regulation respectively. Of course the load on the 24V supply will vary much more greatly.
Both cards are differential input, although that shouldn't really matter.
Is this a bad idea? What are some caveats I am not thinking of?