Hi twins,
My analysis is as follows.
I presume that the motor is a 3-phase induction motor with a squirrel cage rotor as 98% of the motor drives are of that kind as you are also aware.
Since it is induction type, the amount of loading (ammeter reading) depends on the amount of “SLIP” (relative speed with respect to the synchronous speed) that the rotor is subjected to. That means,
“Stator loading (Ammeter reading) is Directly proportional to the amount of SLIP or the speed that the rotor is subjected to “
Therefore when the motor is running at no-load, as an example with the pump uncoupled, we can see only a small loading in the ammeter just because that the rotor is running ONLY against the bearing friction and fan windage which is very very low.
But if somebody tries to stop the rotor by holding it forcibly using a piece of wood or some other arrangement then the rotor is allowed to turn slowly with the full voltage applied to the stator. That means the so called “SLIP” or the relative speed to the syn. speed is increased. As a result the stator takes more “Amps”. If we lock the rotor at this moment it takes about 6 x full load name plate current till the protection operates.
Now your motor is not subjected to either no-load or locked rotor condition as explained earlier. But it takes about 67% ( 6.4 Amps) of the name plate current of 9.5 Amps and also balanced in all three phases. Where does that energy go? It is used to push the flow not to the original amount but to an amount proportional to 64% motor loading. But there may be a small clog or block down the discharge line and NOT at the impeller, which has reduced the nominal flow by 37%.
So make arrangements to remove the clog or the block down the line and then the motor will give you the original flow that means the original ampere meter reading.
Therefore the ammeter reading shows you whether the motor is running or not.