Dear Mr. Mbrooke
Q1. Do analog amp meters have a current limitation?
A1. Yes. Reference IEC 60051, or latest for detail.
In brief, requires over-current factor:
a) up to 1.20 times for 2h for all accuracy class,
b) 2 times for 0.5s for Class 0.5 or less,
c) 10 times for 0.5s for Class 1 accuracy and above,
Caution: Over-current than above or longer duration may damage the meter.
Q2. Basically I want to monitor leakage current on a 3 wire system. A, B, C meters 0-2000 amps, Ground meter 0-30 amps, possibly 0-5 amps range. For this application would I use metering CTs or protection CTs?
A2. Reference IEC 60044-1, or latest for detail.
a) You may use a measuring CT 2000/5 A or 1 A, alternatively a 2500/5 or 1A; Class 1 or 3. These CTs would saturate >2 times. Refrain from using [protection] CT, as it would be more costly and higher chances of damaging the meters during short-circuit.
b) A,B,C ammeters 0-2kA for 2000/x CT or 0-2.5kA for 2500/x CT,
c) ammeter for ground-fault 0-30A or 0-60A.
Q3. "... what if I get a persistent ground fault over 30 amps? Will my meter burn up?"
A3. See above A1. a) a 0-30A ammeter shall be able to withstand at 1.2x30A for 2h. If you use a 0-30A [long range 240 deg] moving-coil ammeter, you should be able to read as low as 5A.
BTW: a) a [moving-iron 90deg] meter would not give good resolution at very low end,
b) If it is observed that persistent > 1.2 x 30A, a 0-60A meter may be selected,
c) for a 2kA system, a persistent ground-fault > 1.2 x 30A is NOT acceptable!
Q4. How will the burden of each meter effect the others under normal and GF conditions?
A4. With a 2000/5A or 1A measurement Class 1 or 3 CT, the burden would be >5VA. The meter burden would have no problem for a CT having burden >5VA.
BTW It is important to earth the CTs. It shall be earthed at [one point] only.
Che Kuan Yau (Singapore)