deedo1124

Electrical
Dec 27, 2007
17
Designing some motor feeders that are routed in rigid steel conduit on an outdoor piperack. I am confused as what to use for the ambient temperature to determine if ampacity adjustment is required. Should I use the warmest average summer monthly high temperature, the areas record high temperature record, or other.

Thanks
 
Replies continue below

Recommended for you

The project is located in San Antonio. The motors are large 480V gas compressors and vacuum pumps.
 
NEC 310.15..2.c (2008) applies to roof installations but may offer some guidance.

Alan
----
"It’s always fun to do the impossible." - Walt Disney
 
Wareagle

Thanks for the link. This will be very helpful.
 