Ambient air temperature for underground cable sizing
Power0020
AU
Tables show derating factors for soil temperature, and ambient temperature, should I consider two derating factors in the case of underground cables? one for soil temperature and the other for ambient temperature? or one only for this type of installations (soil temperature).
One only per IEC, determined by surrounding medium.
The temperature of the captured air in the duct [it is not so important-usually is taken as 60oC] and the earth temperature [it is the most important] in both calculation methods [IEC 60287-2 and Neher and Mc Grath methods].The air temperature is not involved in underground power cable temperature calculation.
though the equivalent circuit shows the ambient as heat sink with fixed temperature (the soil around the cable heats up due to cable current!), I checked Neher and Mc Grath paper and it shows Ta as ambient temperature or earth temperature.
 http://files.engineering.com/getfile.aspx?folder=7e43af40-1947-488c-9ec2-8ec81c330ac8&file=cymcap.png
First of all it is not from the actual Neher and Mc Grath paper, but from "Calculation of Underground Cable Ampacity” by Francisco de Leon -by-the way it is a very good article, in my opinion. The figure 3 and 4 explain the Neher and Mc Grath general technique by subdivided studied area in layers. So tambiant could be air, ground, water [?] and other temperature.
This paper contains the instructions how to use CYMCAP computer program to calculate ampacity and temperature rise of underground power cable-directly buried or in ducts.