pugap--
Are we absolutely sure we're not talking about winding resistance? Winding insulation is generally measured to a ground reference using a megohmmeter and typical measurements on new motors are in the gigohm range. It may be measured with what is referred to generically as a "hipot".
For field maintenance purposes, no motor should be put back in service with less than one megohm resistance, with a rule of thumb being one megohm of resistance per thousand volts of operating voltage. New equipment should be MUCH higher.
Winding resistance, however, is measured from lead to lead on the available motor windings. Measurement of resistance of copper is temperature-sensitive, but should be not too critical with equipment at ambient temperatures in normal maunufacturing facilities. However, being of lower ohmic value, it is not unlikely that the addition of external connections and wiring will make a measurable change to the measured values as aopposed to measurements taken directly at the motor leads.
If I am incorrect and you ARE referring to insulation tests, and your measured insulation resistance to ground for the motor and external circuitry is in the 40-80 ohm range at the voltages you reference, there are some investigations to make: first, disconnect and test the motor. It should be in the high megohm range to ground. If so, then investigate the wiring and motor controller.
Unless I'm missing something in this long distance discussion, no part of the motor power circuit should have this low an insulation resistance to ground.
old field guy