To attempt to add some clarity:
ALF = Accuracy Limiting Factor is used for protection class CTs and it is the number times rated current that the stated accuracy is good up to. For example, 5P20...5 is 5% accuracy class and 20 is ALF. Meaning the CT will maintain 5% accuracy up to 20 times rated current with rated burden applied. In practice, it means that the CT won't saturate at 20 times rated current with rated burden applied.
ISF = Instrument Security Factory is used for metering applications. Normally something like 0.2Fs5 - 15 VA. That means that the CT is designed to saturate at 5 times rated current in order to protect the meter. This kind of rating only exists in the IEC-based world and not in ANSI/IEEE.
Continuous Thermal Rating Factor (often called Rating Factor) is the number of times rated current that the CT can be operated at and not exceed the temperature rise/thermal limits given in the standard. It also becomes the upper limit of the metering accuracy class.
Example CT, 200:5A, 0.3B0.5, RF2.0
For this CT, the CT can be operated continuously at 400A (200A * RF2.0) without exceeding temperature rise limits...in the IEEE world, unless stated otherwise, this is based on a 30C average ambient temp over a 24 hr period, not to exceed 40C peak temp.
Also, this means that the CT is guaranteed to be 0.3% accurate (in the class) from 200A to 400A primary (rated to rating factor) and 0.6% accurate (in the class) from 200A down to 20A (Rated down to 10% rated). This is perhaps the most misunderstood and misapplied rating that we see in CTs. In the IEEE world (and even in IEC world) CTs are meant to be / and should be operated above the rated current.