Are you sure that the CFM you posted is for the outside air, or is that the total CFMs of the units? Either way, your required quantity of OA is no doubt much higher than 2,400CFM. Watch your louver sizing by the way. I would not go higher than 500FPM at the louver to avoid pulling in snow, rain, etc.