Air Gapping Electrical 2

Status
Not open for further replies.

carterav

Mechanical
Aug 13, 2010
14
Does anyone know of any standards that provide direction about how to air gap electrical to prepare for D & D?
 
Replies continue below

Recommended for you

Dungeons and Dragons?

Air gap?

Generally if work is to be done on electrical equipment it is grounded, not "air gapped".
 
Decommishioning and Demolition.

The MCCs will be locked out and 'Air Gapped'.
 
Air gapped?

I, too, would like to know what that term means.

Goober Dave
 
All I have found is the following:

Air Gap: a physical separation that isolates a connection to a voltage source or potential. Reconnection of physical separation shall require extreme effort, or shall be impossible.

physical act of cutting a 12” to 24” section of raceway/cable. AIR GAPPED.

I can't seem to find anything in the NEC or IEEE and I was hoping I could get some help from this site.
 
Labels are applied to the Air Gapped conduit/cable, utility or equipment scheduled for dismantlement activities.

Sorry for the misspell Dave. I should have said Decommissioning and Demolition (D & D).
 
Ah, thanks!

I've never run into this, but you're in the right forum. Someone with experience will answer soon I bet.

Good on ya,

Goober Dave
 
The demolition guys like to see a physical separation between whatever they are working on and whatever they are not (supposed to be) working on. That's where the term 'air-gapped' comes from. We would probably trust a locked breaker, but a visible gap in cables, pipes, etc gives them a visual and definite disconnection from any type of service. I've also heard it described as 'blue sky', although in this part of the world they would wait a long time. [smile]

As for standards, I'm not aware of any. The demo guys don't trust normal isolation devices, so the standard becomes 'whatever they will accept'. Most will accept a gap of a few inches, as long as it is clearly visible.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
So, everything visible is "air gapped" but the source of power that comes in out of the slab is invisible and therefore left in place. Nice. Like I mentioned, visibly grounded is so much more effective.
 
I am also with Mr. Scotty. I have also seen that while doing any maintenance people believe what they see. Air gaped between contacts is something which people can trust for safe working.

I have seen people preferring breakers with fuses over MCCB as that can takeout the fuses and put them in pockets while working. :)
 