air flow metering
LdPmtc
11
what is the more practical ways of measuring air flow in ducts and at diffuser outlets
please let us have your oppinion?
1. Hire a certified test and balance contractor.
2. Standard flows in duct is best with a pitot traverse. How to measure flow
3. Grilles are measured with a flow hood. Such as
4. Smacna has an excellent testing and balance publication.
Balometer for measuring airflow in diffusers, pitot tube for measuring airflow in ducts.
See Alnor for balometers
how practical is it use a pitot tube to determine duct velocity? my concern is if the pitot tube is not held 100% perpendicular with the air stream, how accurate is the velocity reading?
It that concerns you, use a pot head pitot which is less sensitive to yaw angles.
B.E.
An annubar is less sensitive to variations in the flow profile, in that it averages. Similar fundamentals to a pitot traverse, but can be used for permanent installation. Oft-used in VAV measuring stations.
Flow hood is the only good way for diffusers.
what is your experience of using a hot wire anemometer for measuring inline duct velocity (instead of pitot tubes)?
I have used hot wire anemometers in general site testing including duct traverses, but not against a standard.
They usually list in around 5% accuracy and are not as directional as a pitot. Gut feeling is that the hot RTD resistance measurement would be more robust than a low static dp, and thus more likely to be accurate between trips to the lab.