Air Coolers: Viscous Service Issue and Thermal Shock Issue

Status
Not open for further replies.

thermmech

Mechanical
Dec 13, 2004
103
I would appreciate any advice you could give re:

1. On my project, there is an aerial cooler cooling bitumen. Viscosity of bitumen at the outlet > 50 cP. Allowable pressure drop = 600 kPa which is used in full.

API 661 recommends that air coolers do not be employed if fluid outlet viscosity > 50 cP.

I have employed in the design of this unit every possible good design practice I could think of (deep tube bundle, 2 or 3 passes per row, large diameter tubing, dual recirculation ducts, large allowable pressure drop, etc.) - however, I am still worried about the possibility of "unstable flow" phenomenon. What is your particular experience with aerial coolers in high viscosity services?

2. The same project: there is a possibility of an upset condition that could introduce hot (265°C) hydrocarbon fluids into AC and S&T heat exchangers. Ordinarily, these exchangers are operating at temperatures of 80 - 150°C.

Is there a possibility of any adverse effects on the tube-to-tubesheet joints of these exchangers due to introduction of these hot fluids during upset in the plant?

AC joints are 2-grooved & expanded.
S&T joints are 2-grooved & expanded and seal welded.
 
Replies continue below

Recommended for you

It appears that you have done all of the right things. The most important design feature is the relatively high pressure drop. A low pressure drop gives maldistribution of the process stream. There needs to be a pressure drop above a certain value. I have sucessfully designed this type of oil cooler with pressure drops in the 500 kPA range.

Watch out for a temperature change across the inlet sections of over 200 C. if this occurs, the tubes will probably pull out of the tubesheet. For air coolers, use a split header design.
 
You might also go with cocurrent flow (hot fluid into bottom of air cooler; cold fluid out at top). Also, consider a means of adding heat (such as a steam coil) to the air.
Doug
 
djack77494, thanks for input.

Steam coil is provided for start-up only, and it is cost-prohibitive to go with cocurrent-flow configuration.

Regards,
Sean
 