Thanks for the reply. I've read API RP521 but I did not find anything specific concerning the SAR. I am having a problem backing into the design criteria for one of our air assisted flares. I calculated the amount of air that I need for stoichiometric combustion, assumed 50% excess air, and came up with a number in the 9,000 #/hr range. Let me back up a little. The flare stack was supposed to be designed for smokeless operation at 13,000 mscfd of propane. It has never met design. Not even close. I'm a rather hard headed individual. To test what the capacity actually was I connected a meter tube and valve to the vapor space of our propane tanks and to the flare system. Flow tests indicated that 250 mscfd was enough to make the flare smoke. At first I thought that we did not have enough air. After doing the calcs it appears to be a problem with the tip. The contractor is going to make the flare right for us by changing the tip and installing a new blower that is designed to flow 180,000+ #/hr. Now I am really confused. That is a considerable amount of air. I find it a little hard to believe that they are going to supply that much air for this case.
To get stoichiometric I used this formula in a spreadsheet to get #/hr rqd at 50% excess air. Did I miss something?
28.964*(C1mols*2)+(C2mols*3.5)+(C3mols*5)+(iC4mols*6.5)+(nC4mols*6.5)+(iC5mols*8)+(nC5mols*8)+(C6mols*9.5)*(1.5)
The component multipliers were derived from:
2CnH(2n+2) + (3n+1)O2 ---> 2nCO2 + (2n+2)H20
Thanks
Mike