[COLOR=#CC0000[i]]"...#1. If the switch mounting foundation floor is not prefectly levelled does manufacturers allow using shims to adjust so the swithgear line up is on level surface....#2. Is there anybody switchgear manufacturer offering field adjustable support feet for this application?..."[/i][/color]
1. The floor is not expected to be perfectly levelled. It is neither the owner nor the switchgear manufacturer's obligation, but the site installation contractor scope to shim to level and vertically, including bolted up various sections/panels.
Note: The owner does NOT have to pay for the shimming material, including bolt-down bolds and bolts between sections.
1.1 However, if you are the owner and also the site installation contractor, you pay for the shim, bolts etc....NOT the switchboard manufacturer.
2. NO. It is of very small uneven gap which is always expected at site. It is the responsibility /scope of the site installation contractor. The switchgear manufacturer cannot predict the levelling thickness and the location.
Che Kuan Yau (Singapore)