AusLee
Electrical
- Sep 22, 2004
- 259
Hi,
I have a 1000 kVA generator and a 1000 kVA transformer.
They both feed an open transition ATS in the main distribution board.
Since it is open transition, only 1 source is active at a time. The short circuit rating of the MDB is 30kA, sufficient for either source.
Now the client wants to substitute the open transition of the ATS to a closed transition ATS. The time both sources are online together during the closed transition is aroun 100 milliseconds. Will this require subsituting the whole MDB with another one with double the kA rating?