rockman7892
Electrical
- Apr 7, 2008
- 1,178
I am trying to determine weather or not I can add additional loads to a 480V MCC. The MCC has a 2000A bus and is protected by a 2000A breaker.
I added the loads using 1hp = 1kVA. I took 25% of largest motor and 125% of combined continuous non-motor loads. When adding in the additional loads I come up with a total connected load of 2009A.
This 2009A is obviously greater than the 2000A bus but does not account for any diversity factor. I'm sure others here have been in similar situations in the past and wanted to see what the rule of thumb was for this type of situation.
How are breakers for welding receptacles which typically aren't connected all the time figured?