rockman7892
- Apr 7, 2008
- 1,176
We currently own our substation which recieves power from the utility at 240kV and steps it down to 4.16kV via a 15/20/25 MVA Delta-Wye transformer. I have attached a 3-Line diagram of our existing substation, showing all of the equipment, and relaying associated with this substation. The bottom of the drawing shows where the cables terminate onto the substation bus in order to feed the incoming breaker and 5kV lineup on our existing plant. The existing plant has about 18MVA of connected load.
We are proposing building a small grinding plant here on the same site and are in the preliminar stages of looking into how we will power this plant. Right now I am investigating the option of powering this new plant off of our existing substation provided there is capacity. We are in the preliminary planning stages, and I wanted to see if it is even feasable to tap of our existing substation before we press forward with any hardcore engineering.
Based on the provided drawing and relay scheme I was wondering the following:
1) Can we tap off of the Transformer LV Bus at the proposed point indicated on the drawing to feed our new plant with a proposed connected load of 2MVA provided there is capacity (The capacity is a big if at this point)
2) If the proposed tap point is not feasable, is there another location on this substation arrangement that could be tapped to feed the new plant?
3) Based on the relay scheme, would any new circuit interrupting devices or relaying need to be added or re-arranged.
Again we are only in the preliminary planning stages and want to look at the feasability of this before we move on. I appreciate any comments, thoughts, ideas.