We have a 13.8 kV switchgear with a main breaker, a utility metering and the 4 feeder with a breaker each. All the network is underground.
We want to add a feeder, but we cannot just add a cell at the end of the switchgear because of space. We can only add a cells 100 ft away from the switchgear
so how can we do this. We thought to connect a teck cable just after the utility metering, and run it 100 ft away to another cells and there put a breaker. But the teck cable will only be protected by the main breaker of the switchgear, and i'm not sure we can do this, can we? we are in Canada and i didn't see anything about it.
Another option is to connect the new feeder on the load side of a breaker with another feeder already there. Maybe add a set of ct on each feeder to be able to locate a fault. But there again, maybe we will have a space problem.
Do you have any idea?
thanks
We have a 13.8 kV switchgear with a main breaker, a utility metering and the 4 feeder with a breaker each. All the network is underground.
We want to add a feeder, but we cannot just add a cell at the end of the switchgear because of space. We can only add a cells 100 ft away from the switchgear
so how can we do this. We thought to connect a teck cable just after the utility metering, and run it 100 ft away to another cells and there put a breaker. But the teck cable will only be protected by the main breaker of the switchgear, and i'm not sure we can do this, can we? we are in Canada and i didn't see anything about it.
Another option is to connect the new feeder on the load side of a breaker with another feeder already there. Maybe add a set of ct on each feeder to be able to locate a fault. But there again, maybe we will have a space problem.
Do you have any idea?
thanks