May 7, 2013 #1 powersoff Electrical Joined Jan 16, 2008 Messages 80 Location US Does anyone have suggestions for ACS355 VFD that intermittently faults on overvoltage? At the time of the last fault voltage was 831 volts. This fault is happening once every couple of days.
Does anyone have suggestions for ACS355 VFD that intermittently faults on overvoltage? At the time of the last fault voltage was 831 volts. This fault is happening once every couple of days.
May 7, 2013 Moderator #2 waross Electrical Joined Jan 7, 2006 Messages 28,817 Location CA What is the load? What is the voltage? What HP? Do you ramp down the speed quickly? Bill -------------------- "Why not the best?" Jimmy Carter Upvote 0 Downvote
What is the load? What is the voltage? What HP? Do you ramp down the speed quickly? Bill -------------------- "Why not the best?" Jimmy Carter
May 8, 2013 Thread starter #3 powersoff Electrical Joined Jan 16, 2008 Messages 80 Location US Blower Motor 497VAC Input 20hp 30 seconds deaccel time DC bus voltage during running is observed around 680 Upvote 0 Downvote
Blower Motor 497VAC Input 20hp 30 seconds deaccel time DC bus voltage during running is observed around 680
May 9, 2013 #4 jraef Electrical Joined May 29, 2002 Messages 11,368 Location US Do you have an idea of what is happening when it trips on OV? As in during Run, during Decel, while Off? "Will work for (the memory of) salami" Upvote 0 Downvote
Do you have an idea of what is happening when it trips on OV? As in during Run, during Decel, while Off? "Will work for (the memory of) salami"