powersoff
Electrical
- Jan 16, 2008
- 80
I have a blower fan Motor:20hp, 460, 22fla, 1.15sf, codeJ
DesA,ClassB.
The ABB ACS350 VFD controlling fan motor is occasionally faulting on a overcurrent.
It faults when automatically starting from a dead stop.In the fault history I can see the current at 51 amps. The drive is then powered down fault clears and motor restarts fine.
The acceleration time is 5 seconds.
Any ideas?
I have a second question is the current that is displayed in the HMI of the VFD dependent on parameters?
For example if I change the Nominal Motor Volts or current will the Current reading change on the HMI?
DesA,ClassB.
The ABB ACS350 VFD controlling fan motor is occasionally faulting on a overcurrent.
It faults when automatically starting from a dead stop.In the fault history I can see the current at 51 amps. The drive is then powered down fault clears and motor restarts fine.
The acceleration time is 5 seconds.
Any ideas?
I have a second question is the current that is displayed in the HMI of the VFD dependent on parameters?
For example if I change the Nominal Motor Volts or current will the Current reading change on the HMI?