how often should rfive eigths rebar be tied in concrete
foundation wall 12inches vertical 12inches horozontal ?
 
Concrete Reinforcing Steel Institute – “Placing Reinforcing Bars”

Wall Construction page 11-11

“The horizontal and vertical bars are wired securely to each other at sufficiently frequently intervals to make a rigid mat. Tying is required depending on upon the size and spacing of bars, but not less than 3 ties to any one bar, and, in any case, not more than 4 to 6 ft apart in either direction”
 