There is some discrepancy among long time engineers and new engineers in my office about development length:
The ACI 318-08 code states that equation 12-1 is the "general development lengt equation." In this equation there is a term of ((cb+Ktr)/db). The Ktr term is "a factor that represents the contribution of confining reinforcement ..." Section 12.2.3 allows for this term to be taken to 0. The cb term is a spacing and cover term defined in chapter 2 with no reference to confinement in the definition. And db is the diamter of the bar. The term ((cb+Ktr)/db) must have a value of at least 1.5 but must not exceed 2.5. I have used this equation many times and usually get a value for this term of greater than 2.5 so end up using 2.5 in the development length equation. HOWEVER, when using 2.5 in this equation, the development length ends up being about HALF the value of that when using the equations from the table in section 12.2.2. When the ((cb+Ktr)/db) term is taken to be the minimum value of 1.5, the value for development length ends up being the same that you would get if you used the table in section 12.2.2.
The question becomes: Can you use the "general" development length equation with the term ((cb+Ktr)/db) assuming Ktr to be zero when you don't have confining steel in a case such as a wall or slab? Is the Ktr term the confining term or is the ((cb+Ktr)/db) the confining term, even though it is not defined as such?
The ACI 318-08 code states that equation 12-1 is the "general development lengt equation." In this equation there is a term of ((cb+Ktr)/db). The Ktr term is "a factor that represents the contribution of confining reinforcement ..." Section 12.2.3 allows for this term to be taken to 0. The cb term is a spacing and cover term defined in chapter 2 with no reference to confinement in the definition. And db is the diamter of the bar. The term ((cb+Ktr)/db) must have a value of at least 1.5 but must not exceed 2.5. I have used this equation many times and usually get a value for this term of greater than 2.5 so end up using 2.5 in the development length equation. HOWEVER, when using 2.5 in this equation, the development length ends up being about HALF the value of that when using the equations from the table in section 12.2.2. When the ((cb+Ktr)/db) term is taken to be the minimum value of 1.5, the value for development length ends up being the same that you would get if you used the table in section 12.2.2.
The question becomes: Can you use the "general" development length equation with the term ((cb+Ktr)/db) assuming Ktr to be zero when you don't have confining steel in a case such as a wall or slab? Is the Ktr term the confining term or is the ((cb+Ktr)/db) the confining term, even though it is not defined as such?