Thank you all for your feedback.
I have also sent my question to ICC for interpretation, and here is their response:
Thank you for query below regarding blast loading in the 2018 IFC and the 2018 IBC.
The interaction of a real world blast with a structure can result in very complex inelastic dynamic behavior.
For buildings that house hazardous processes, building codes require special safety considerations. The 100 psf noted in section 911.2 of the 2018 IFC is intended to be the design load minimum internal pressure. This design requirement dates back the legacy codes: For example, the Uniform Building Code stated that “walls, floors and roofs separating a use from an explosion exposure shall be designed to resist a minimum internal pressure of 100 pounds per square foot in addition to other conventional loads.”
Naturally, such structures need to be designed and detailed to resist progressive collapse.
Unfortunately, both the 2018 IBC and ASCE/SEI 7-16 do not explicitly define how to handle the defined blast loading.
ASCE/SEI 7-16 commentary section C1.3.1.3 states, “The alternative procedures of Section 1.3.1.3 may be used to demonstrate adequacy for one or more design loads, while the standard procedures of Sections 1.3.1.1 and 1.3.1.2 are used to demonstrate adequacy for other design loads. For example, it is relatively common to use the alternative procedures to demonstrate adequate earthquake, fire, or blast resistance, while the standard prescriptive procedures of Sections 1.3.1.1 and 1.3.1.2 are used for all other loading considerations.”; hence, ASCE/SEI 7-16 recommends using Performance-Based Design Procedures of ASCE/SEI 7 section 1.3.1.3.
While blast loads are dynamic, in some circumstances it makes sense to use equivalent static blast loads for design. Blast loads are typically combined with gravity loads and load factors are set equal to 1.0 and one can use a more realistic guess at day-today live load. Hence, in addition to the typical design load combinations of IBC and ASCE/SEI 7; ASCE 59-11 (Blast Protection of Buildings) recommends the following additional two combination where B = Blast loading:
• 1.0 B + 1.0 D + 0.5 L
• 1.0 B + 1.0 D + 0.2 W[/color]