Hello Scdaiwei,
The first picture is not perfectly clear to me.
- What is evident is that the part in the bottom right is a filter/reducer to make sure you have clean supply pressure that is not overpressuring your actuator.
- The item in the bottom left looks like a selector valve. Normally used for manual override or testing the valve.
- In the top left you have a volume booster. Included to increase the operating speed of the actuator.
- Top middle can be several things. I am not sure, but I expect that these are high capacity filter/reducers.
- Top right looks like just a gauge on a cross-connector. To show the inlet pressure.
The second picture is easier.
- On the right you have a Fisher booster type 2625 as mentioned by Igreca. This is also used to increase the operating speed of the valve.
- On the right is a Fisher trip valve type 377L. This is used for making sure that the valve has a fail function when the supply pressure is lost. The fail function can be fail lock by blocking all exits or fail open/close by connecting one exit to an accumulator. Since the boosters are placed after the trip valve it must be fail open/close, because the fail lock function is overruled by the boosters.
TIP:
You can look at the nameplates of the equipment what the manufacturer and model is.
Best regards,
Terje