Does AC23 on an isolator mean the isolator is capable of breaking (
Emergency stopping an inductive load?
 
See Link.

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips.
 
Dear Mr. Jk1996 (Electrical)(OP)10 Nov 21 22:14
"...Does AC23 on an isolator mean the isolator is capable of breaking (
Emergency stopping an inductive load? "

1. Refer to the "link" as advised by learned Mr. xnuke.
2. Yes, it can. See also IEC 60947-3 on (switches, disconnectors,....) where it states the (AC-23A, 23B ) typical applications [switching of motor loads or other highly inductive loads]
Che Kuan Yau (Singapore)
 