Being on the design (rather than the install side) I am certain that some of the installers (and people with a lot of field install experience like
imok2) will have different comments.
You can access the Carrier manual for this unit (which you should have if you are going to design a system with it) at
I assume that you DON'T have a horizontal unit. The manual (for the 50TFQ units) states that you can install it without the roof curb but it appears that you will have to essentially build what amounts to a roof curb anyway. Where I have worked we always have specified the factory roof curb (which appears to be shipped with these units) for several reasons:
1) It will be the correct size which prevents a mistake building one from scratch in the field.
2) The general contractor can build the roof curb into his roofing system. This is usually done by the general contractor and NOT the HVAC contractor. This helps prevent contractor coordination problems.
3) The labor cost will be much lower with a factory built part than a field built part.
4) It allows the engineer to use a standard mounting detail which references the factory built roof curb.
5) You don't have to analyze any strength requirements for a custom roof curb.
6) Standard vibration isolators (which is in our standard detail) will fit.
7) It lifts the unit slightly above the roof to prevent leakage problems with the roof, allow easier condensate connections (with trap) etc.
8) It gives you something to attach the ductwork to.
I am certain that there are a lot more reasons. I noticed that this is a standard efficiency unit. You may want to consider 50HJQ.
I have attached the relevant pages of the installation manual obtained from the Carrier site.