I am assuming that you are designing a new winding, not just reconnecting a wye wound motor to delta (the latter one will kill the winding).
Having said that, I have seen (and rewound) delta connected 6.6 KV stator windings for 3.5 MW/4 MW boiler feed pump motors. Though many MV motors are star connected (thereby reducing the voltage stress across phase to ground), if the MW is high (meaning more current requiring heavier copper cross-sections, which are difficult to handle), a wye connection is discarded in favor of delta connection.