rockman7892
We are getting ready to commission a 480V 350hp motor connected to a VFD for a cement kiln application. AC drive is 750hp drive. Although we plan on bringing a drive engineer On-Site to assist with the startup, I wanted to gain a little insight for myself the best way to setup the the drive control mode for this application.
The motor has an encoder, and the control methods avaliable in the drive a V/Hz and FOC (no sensorless vector). I'm assuming for this application we would want to have the drive in the FOC mode, is this correct? I know the kiln will have a very high starting torque so what is the best way to accomplish this? The motor has a maximum running rated torque, however it also has a "1 min" rated torque. What is the purpose of this 1 min rating? Is this a rating to be able to provide full torque a zero speed with the motor datahseet implies.
Just wanted to see if others have had experience with AC drives on a kiln application who would be willing to share their experiences or insight.