It is very doubtful that you could use the switch for DC service at that rating. Contacts are normally severely derated for DC interrupting duty unless they have magnetic blowout coils or other means to assist the interruption. If you want to see quite an arc, try interrupting 80 amps DC at 125VDC with contacts that are rated for AC. It's usually pretty spectacular!