Hello guys,
A circuit has a small load of 75 kVA at 4.16 kV, and a very high shortcircuit level, around 50 kA.
If we choose the CT in order to "see" the load current it will be a very low ratio (let's say 150/5) but, it will not held 100 A secondary neither saturation criteria.
However, taking into account saturation and less than 100 A sec, the ratio needs to be so high that relay will not see any load, I mean, the secondary current has a magnitude so small that the sensibility of the relay does not see it and then, it will consider as the circuit were open.
What options should we consider to solve this?
Any idea is welcome!
Best Regards