WARNING! To avoid danger, or damage to the drive, on IT systems, corner-earthed TN systems and residual current circuit breakers, see section Disconnecting the internal EMC filter on page 45.
R5
X0013
Power output to motor
(U2, V2, W2)
Power input
(U1, V1, W1)
GND
F2
F1
F1
PE
GND
PE
Power output to motor
(U2, V2, W2)
F2
R6
GND
Power input
3-phase: U1, V1, W1
1-phase: U1 (live), W1
Installing the drive 45
ACH550-01 User's Manual
Disconnecting the internal EMC filter
On certain types of systems, you must disconnect the internal
EMC filter, otherwise the system will be connected to earth
potential through the EMC filter capacitors, which might cause
danger, or damage the drive.
Note: When the internal EMC filter is disconnected, the drive is
not EMC compatible.
The following table shows the installation rules for the EMC filter screws to connect or disconnect the filter, depending on the system type and the frame size. The locations of the screws EM1 and EM3 are shown in the diagram on page 43. The location of the screws F1 and F2 are shown in the diagram on page 44.