Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

AASHTO Guide Spec, SDC A

Status
Not open for further replies.

Phred404

Structural
Joined
Dec 16, 2015
Messages
2
Location
US
Looking at 8.8.9 of the Guide Spec, #5 bars are required for Lateral reinforcement for longitudinal bars #10 or larger. Given that the Guide Spec has requirements for the hoop spacing, why would they require a larger lateral reinforcement bars? We can meet the spacing requirement with a tighter spacing of #4 bars. This is for SDC A with SD1>1.0
 
Right. That pesky decimal point. SD1=0.116. This is greater than 0.10 and our Site Class is D, so SDC is A(high)
 
Had a feeling you may have misplaced that decimal haha. I'm guessing it has something to do with what they mention in the Commentary for that section; in addition to providing shear strength, the hoops also serve to brace the longitudinal column steel.
 